    Question for sparkies: Heated towel rail, lighting circuit

    One of my next projects involved putting in a heated towel rail into the bathroom.

    My problem is the only wiring remotely close is a lighting circuit. It is current not protected by an RCD. Laying in a feed from a power point is going to be a major.


    The heated towel rail uses a maximum of 60W. It I change the fuse for the lighting circuit to an RCD, can I feed a heated towel rail from a lighting circuit?

    When I have questions, I usually refer to the guide "New Zealand Electrical Code of Practice for Homeowner/Occupier’s Electrical Wiring Work in Domestic Installations", but I can't find the answer I'm looking for.
    http://www.med.govt.nz/energysafety/...202004%20.pdf/

    ps. The electrical connection will be in "Zone 3".

  2. #2
    Join Date
    3rd March 2008 - 11:55
    Bike
    ST2 NZ250
    Location
    The evil flatlands
    Posts
    2,316
    From reading the link supplied - In zone 3 you're fine as long as the lighting circuit has an earth, no IP rating or RCD required for switches or appliances in Zone 3, a PCU is not a socket outlet.

    Quote Originally Posted by med
    6.7 ELECTRICAL APPLIANCES (HEATERS, HEATED TOWEL RAILS, FANS ETC)6.7.1 The following must apply to the installation of electrical appliances in the classified Zones:
    (a) Zone 0: electrical appliances with the required degree of protection, IPX7; and, specifically designed for Zone 0 and installed to the manufacturerer’s instructions; and, operated from a safety extra-low voltage system not exceeding 12 V AC. or 30 V ripple free DC, with the supply source located outside Zone 0;
    (b) Zones 1 and 2: IPX4;
    (c) Zone 3: no IP rating required.
    NOTES: 1. Instantaneous water heaters installed in Zone 1 would be mounted on the fixed plumbing connection.
    40
    2. Extractor fans installed in Zones 1, 2 or 3 could be mounted in the walls or in or on the ceiling of the different Zones.
    3. Electrical appliance heaters that you install in Zones 1, 2 and 3 must be mounted not less than 0.3 m above the floor, or have the element totally enclosed in metal (e.g. a heated towel rail).
    4. The control switch for these appliances, if mounted externally, must have the required degree of protection for the Zone.
    For convenience sake I've always put a switch with a neon for the towel rail in the plate with the light switch.
    Riding cheap crappy old bikes badly since 1987

    Tagorama maps: Transalpers map first 100 tags..................Map of tags 101-200......................Latest map, tag # 201-->

  3. #3
    Join Date
    19th July 2007 - 20:05
    Bike
    750 auw
    Location
    Mianus
    Posts
    2,247
    Just run an extension cord bro!

  4. #4
    Join Date
    6th May 2012 - 10:41
    Bike
    invisibike
    Location
    pulling a sick mono
    Posts
    6,054
    Blog Entries
    4
    are you switching the rail?

    either way, as long as earthy gets eartheyed there should be no problem. general lighting circuits are not earthyed.

  5. #5
    Join Date
    26th January 2008 - 07:37
    Bike
    91 R80GS
    Location
    Nelson
    Posts
    5,225
    Sparky here. if in doubt get a sparky! Don't listen to guys that aren't as i overheard a carpet layer confidently telling an old fella how to kill hiself with wiring.

    That said just get a doubly insulated heated towel rail - but get a sparky to check it. Most sparkies are more thna happy for the owner to mount them as they're a pITA but wiring them in is a piece of cake.


    It's debatable that RCDs work without an earth.
    In life as in dance Grace glides on blistered feet

  6. #6
    Join Date
    26th January 2008 - 07:37
    Bike
    91 R80GS
    Location
    Nelson
    Posts
    5,225
    Quote Originally Posted by Akzle View Post
    are you switching the rail?

    either way, as long as earthy gets eartheyed there should be no problem. general lighting circuits are not earthyed.
    That is absolute crap!
    In life as in dance Grace glides on blistered feet

  7. #7
    Join Date
    20th June 2011 - 20:27
    Bike
    Dog Rooter, 1290 SDR
    Location
    Marton
    Posts
    9,851
    Really? Heated towel rail?

    Guess you ride a Honda.
    Quote Originally Posted by Katman View Post
    but once again you proved me wrong.
    Quote Originally Posted by cassina View Post
    I was hit by one such driver while remaining in the view of their mirror.

  8. #8
    Join Date
    5th December 2009 - 12:32
    Bike
    Yes
    Location
    Yes
    Posts
    3,283
    Quote Originally Posted by nzspokes View Post
    Really? Heated towel rail?
    I went in to Briscoes today and they don't even sell heated towels down here.

    Apparently they don't sell enough shandy in Dunedin to make it worthwhile.

  9. #9
    Join Date
    9th October 2008 - 15:52
    Bike
    RSV4RR, M109R, ZX10R
    Location
    wellington
    Posts
    6,165
    Blog Entries
    1
    Not many towel rails arnt double insulated. If the flex on it is 2 core then it is or the square inside square is on the info label it is double insulated.
    Light circuit is fine. You need a point of isolation within 1 metre of the rail( perminent connection unit is easiest) and this must not be within 450mm of the side of tub,basin,shower etc. The rail can be closer but not its point of connection and switch.

    Rcd protection still works on double insulated appliances.
    It works on a system of balance between phase and neutral. If any power above 30mill amps leaks away and does not return on the neutral the rcd trips. This can be via earth wire or any other path(person works fine). The rcd is designed to do this within a time frame that in MOST cases is none leathal.
    Attached Thumbnails Attached Thumbnails Click image for larger version. 

Name:	viagra.jpg 
Views:	40 
Size:	20.5 KB 
ID:	266756  
    I have evolved as a KB member.Now nothing I say should be taken seriously.

  10. #10
    Join Date
    10th May 2009 - 15:22
    Bike
    2010 Honda CB1000R Predator
    Location
    Orewa, Auckland
    Posts
    4,490
    Blog Entries
    19
    Quote Originally Posted by Akzle View Post
    are you switching the rail?


    either way, as long as earthy gets eartheyed there should be no problem. general lighting circuits are not earthyed.
    Yes, it will be switched.

    Quote Originally Posted by Padmei View Post
    That is absolute crap!
    THr lighting circuit does have the standard 3 core TPS, so an earth is definately available.

    Quote Originally Posted by nzspokes View Post
    Really? Heated towel rail?

    Guess you ride a Honda.
    We still have 4 children living at home, and want to reduce the amount of washing we are doing.

    Quote Originally Posted by mossy1200 View Post
    Not many towel rails arnt double insulated. If the flex on it is 2 core then it is or the square inside square is on the info label it is double insulated.
    Light circuit is fine. You need a point of isolation within 1 metre of the rail( perminent connection unit is easiest) and this must not be within 450mm of the side of tub,basin,shower etc. The rail can be closer but not its point of connection and switch.

    Rcd protection still works on double insulated appliances.
    It works on a system of balance between phase and neutral. If any power above 30mill amps leaks away and does not return on the neutral the rcd trips. This can be via earth wire or any other path(person works fine). The rcd is designed to do this within a time frame that in MOST cases is none leathal.
    It does have the square symbol on it, but the flex coming off it is 3 core.

    I think I'll get an RCD. If it keeps trippping because of the heated towel rail I can always use it somewhere else.

  11. #11
    Join Date
    6th May 2012 - 10:41
    Bike
    invisibike
    Location
    pulling a sick mono
    Posts
    6,054
    Blog Entries
    4
    Quote Originally Posted by Padmei View Post
    That is absolute crap!

    huh?

    i was wondering about all this two core in the roof.... magic earth eh?

  12. #12
    Join Date
    3rd March 2008 - 11:55
    Bike
    ST2 NZ250
    Location
    The evil flatlands
    Posts
    2,316
    Quote Originally Posted by p.dath View Post
    I think I'll get an RCD. If it keeps trippping because of the heated towel rail I can always use it somewhere else.
    RCD is not a bad idea anyway, pretty cheap insurance if you've got 4 kids in the house, it shouldn't trip unless there is a fault somewhere in which case you'll probably be glad you had it.

    Quote Originally Posted by Akzle View Post

    huh?

    i was wondering about all this two core in the roof.... magic earth eh?
    In a lot of cases there is 3 core with earth to the switch, but only 2 core to the light as it's feeding a batten holder which doesn't get earthed.
    Riding cheap crappy old bikes badly since 1987

    Tagorama maps: Transalpers map first 100 tags..................Map of tags 101-200......................Latest map, tag # 201-->

  13. #13
    Join Date
    14th July 2006 - 21:39
    Bike
    2015, Ducati Streetfighter
    Location
    Christchurch
    Posts
    9,081
    Blog Entries
    8
    I thought all electrical hook-ups of this nature are to be done by a qualified sparky by law. You can pre wire etc but the sparky has to cert it. They are taking the DIY out of many things like this and rest assured if you DIY it and burn the house down the insurance company will want to know who wired the towel rail ........

    Then again do you really want some tradie in your house whacking off over over your wifes knickers? Target - what a show eh?

  14. #14
    Join Date
    10th May 2009 - 15:22
    Bike
    2010 Honda CB1000R Predator
    Location
    Orewa, Auckland
    Posts
    4,490
    Blog Entries
    19
    Quote Originally Posted by AllanB View Post
    I thought all electrical hook-ups of this nature are to be done by a qualified sparky by law. You can pre wire etc but the sparky has to cert it. They are taking the DIY out of many things like this and rest assured if you DIY it and burn the house down the insurance company will want to know who wired the towel rail ........
    From Electricity Act section 169, clause 20:
    110. Exemption for domestic electrical work – (1) Notwithstanding anything in section 108 of this Act, the owner of any premises that are occupied or intended to be occupied by that person as a residence for that person, or for that person and members of his or her family, may do any electrical wiring work, or assist in doing any electrical wiring work, in relation to those premises, if–
    (a) That work is within the limits prescribed in regulations made under section 169 of this Act for the purposes of this section; and
    (b) The work is carried out in accordance with the requirements of any regulations made under section 169 of this Act; and
    (c) The work is carried out in a competent manner; and
    (d) While that work is being carried out, no part of the work is connected to a power supply; and
    (e) Where required by regulations made under section 169 of this Act,
    (i) Before connection to a power supply, the work is tested and certified by a registered electrical inspector in accordance with regulations made under that section; and
    (ii) The work is connected to a power supply by such an inspector.
    ps. And it needs to be an electrical inspector, not just a sparky.

  15. #15
    Join Date
    1st July 2007 - 17:40
    Bike
    my little pony
    Location
    shoebox on middle of road
    Posts
    1,522
    Quote Originally Posted by p.dath View Post
    From Electricity Act section 169, clause 20:


    ps. And it needs to be an electrical inspector, not just a sparky.
    So it would be alot simpler just to get a sparky in the first place.