    Shed/workshop queries for tradies

    electricunts:
    shed runs as spur off main building. Breaker inside house is 20a (with earth leak (dipole?) rcd thing), shed board has 2x 15a gpo and 1x 5a lighting circuit. 40a total aye
    House board has 140a total on the face of it, with the 'main' being 3gang 240/415
    this sounds like three phase, which might come in handy in the shed, but 'slike its only one phase going to, yea?
    So, can i put a 40 or 50a breaker inside house, as by the time im making noise with tools im over 20a, and walking over and flipping itd be a cunt.
    Yes/no?
    2, can i drag full 3 phase to the shed? What is code requirement re ducting/poles/conduit?
    Then, presumably i can tap off single phase too?

    Concrete finisher cunts:
    the floor is 6-10 slabs jigsawed together. 80sq meters.
    Total variation over 30mm, chips, holes etc. Plus oil stains and shit.
    Can i hit it with leveller compound? (any prep?) Am i better boxing up and tying another (4") slab on top? Or grinding down 5-10?
    As much as id love to epox it, its probably going to have to deal with mere paint. Only one bay will have trolley jack abusing it as i plan on a gantry. The rest is basically workshop floor, no doubt the odd oil or coolant spill but generally just walked on...

  2. #2
    Join Date
    6th May 2012 - 10:41
    Bike
    invisibike
    Location
    pulling a sick mono
    Posts
    6,054
    Blog Entries
    4
    also, im at the end of the powerlines in the wops. Theres an 8?kva transformer that supplies 3 farm houses and another shed already.
    Got a stack load more lifestylers invading further toward main feed in end so dont know if this is likely to fuck up capacity?

  3. #3
    Join Date
    6th May 2012 - 10:41
    Bike
    invisibike
    Location
    pulling a sick mono
    Posts
    6,054
    Blog Entries
    4
    also, the power box in the shed is some melamine shit, spose i need a proper din one yeah?

  4. #4
    Join Date
    28th May 2006 - 19:35
    Bike
    suzuki
    Location
    lower hutt
    Posts
    8,189
    [QUOTE=Akzle;1130699413
    So, can i put a 40 or 50a breaker inside house, as by the time im making noise with tools im over 20a, and walking over and flipping itd be a cunt.
    Yes/no?
    [/QUOTE]
    the breaker is there to protect the cable, depends on what size cable is running over as to what size protection it needs

  5. #5
    Join Date
    27th March 2006 - 10:29
    Bike
    KTM 1190 Adv R and a bunch of dirties
    Location
    Burglary capital of Unzud
    Posts
    2,879
    Basically circuit breakers / fuses protect the cable. So find out what size the cable is to the shed. There are simple tables for cct breaker size to cable size. Ignore the part about the length, that is for selecting the size of the cable you need in the first place.

    Edit: Wot he said above.
    Quote Originally Posted by Albert
    Two things are infinite: the universe and human stupidity; and I'm not sure about the universe

  6. #6
    Join Date
    20th January 2008 - 17:29
    Bike
    1972 Norton Commando
    Location
    Auckland NZ's Epicentre
    Posts
    3,554
    Quote Originally Posted by Akzle View Post
    also, the power box in the shed is some melamine shit, spose i need a proper din one yeah?
    Ah melamine...drilling old switchboards bring back memories.
    Get a Registered Sparkie to do it so they don't have to quit the industry and work for Corporates like me.
    You get a proper job and COC too.
    Or get that old Post Office workshops bloke from Wanganui to do it.
    DeMyer's Laws - an argument that consists primarily of rambling quotes isn't worth bothering with.

  7. #7
    Join Date
    6th May 2012 - 10:41
    Bike
    invisibike
    Location
    pulling a sick mono
    Posts
    6,054
    Blog Entries
    4
    Quote Originally Posted by jellywrestler View Post
    the breaker is there to protect the cable, depends on what size cable is running over as to what size protection it needs
    looking inside the melamine box... Big.
    Defnitly big.
    To my untrained eye, id run 30a with no drop. Looks slightly smaller than demarc/kwh meter cabling. But this shits probably 60 years old... So..?
    That suggests running new cableh?

  8. #8
    Join Date
    28th May 2006 - 19:35
    Bike
    suzuki
    Location
    lower hutt
    Posts
    8,189
    Quote Originally Posted by Akzle View Post
    looking inside the melamine box... Big.
    Defnitly big.
    To my untrained eye, id run 30a with no drop. Looks slightly smaller than demarc/kwh meter cabling. But this shits probably 60 years old... So..?
    That suggests running new cableh?
    got a camera? if ya have use the fucking thing, are there any crimp lugs on either end of the cable? wont be on the phase, posibbly nuetral at shed end, this may have a stamping on telling you cable size

  9. #9
    Join Date
    6th May 2012 - 10:41
    Bike
    invisibike
    Location
    pulling a sick mono
    Posts
    6,054
    Blog Entries
    4
    bump!

    Hey, anyone wanna buy a hyosung?

  10. #10
    Join Date
    2nd August 2012 - 21:01
    Bike
    1989 Yamaha FZR400
    Location
    North Shore, Auckland
    Posts
    290
    Quote Originally Posted by Akzle View Post
    bump!

    Hey, anyone wanna buy a hyosung?
    I'll give ya 5 bucks and a bag of chips. Scrap that it ain't worth 5 bucks, ill give you the chips for it.


    Sent from my iShit using Tapatalk

  11. #11
    Join Date
    6th May 2013 - 20:16
    Bike
    Red-shifted GT250R
    Location
    Christchurch
    Posts
    225
    Quote Originally Posted by DanielM8 View Post
    ill give you the chips for it.
    I'll give you two bags of chips & part it out to myself as mine shits its panties.

  12. #12
    Join Date
    6th May 2012 - 10:41
    Bike
    invisibike
    Location
    pulling a sick mono
    Posts
    6,054
    Blog Entries
    4
    Quote Originally Posted by Taxythingy View Post
    I'll give you two bags of chips & part it out to myself as mine shits its panties.
    thats why no one's dumb enough to fuken buy them. Oh. Wait on...

  13. #13
    Join Date
    6th May 2012 - 10:41
    Bike
    invisibike
    Location
    pulling a sick mono
    Posts
    6,054
    Blog Entries
    4
    house:
    demarc -> fuse panel ->meter ->??

    The treble breaker in the box says
    63a 240/415v its a 3 gang.
    Is that 63a at 415? (acros 3 phases?) or 63a/phase?
    Old wire in the roof is 7x ~2mm conductors...

  14. #14
    Join Date
    28th May 2006 - 19:35
    Bike
    suzuki
    Location
    lower hutt
    Posts
    8,189
    Quote Originally Posted by Akzle View Post
    house:
    demarc -> fuse panel ->meter ->??

    The treble breaker in the box says
    63a 240/415v its a 3 gang.
    Is that 63a at 415? (acros 3 phases?) or 63a/phase?
    Old wire in the roof is 7x ~2mm conductors...
    use a camera ya useless cunt

  15. #15
    Join Date
    13th March 2006 - 20:49
    Bike
    TF125
    Location
    Hurunui, FTW!
    Posts
    4,430
    Akzle's probably too embarrassed to post pics...
    Attached Thumbnails Attached Thumbnails Click image for larger version. 

Name:	image.jpg 
Views:	34 
Size:	99.6 KB 
ID:	295901  

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •